hhsting
- Glen bunie, md, us
- Junior plan reviewer
I know I had some variation of below question prior but design has change a little and I am not sure about few items NEC 2014 code wise.
Please see attached sketches which show cluster of apartment residential one is Top view and second is Elevation view. The cluster has individual buildings 1 to 6 separated by firewall. Their is outside utility transformer which feed outside service entrance rated switchboard.
The service entrance rated switchboard is three phase, 208/120V, 2250A, that has 3 main breakers and one of them is 1000A main breaker whose load side feeds underground direct buried feeder FDR #1. The FDR #1 is Aluminum 2 sets of 4#500kcmil + 1/0G underground direct buried to Panel P. I understand cable size is off based on 1000A breaker and so is equipment grounding conductor size but telling you whats shown on plans.
Panel P is mounted on outside wall of the cluster as shown in sketch.
Since their is outside feeder into Panel P, Panel P is grounded has grounding electrode system ground rods and water pipe no building steel per NEC 2014 section 225.30. So Panel P has two grounding electrode conductors bare going to water pipe and another to rods.
Panel P then feeds meter stacks in Electrical room #1 inside Bldg 2 and Electrical Room #2 inside Bldg 4 as shown on attached sketch Top view.
I have the following questions:
1. Are the underground cables FDR #1 allowed to be direct buried or not? Is their a section that says they must be in conduit underground
2. This is residential apartments. Since their would be bare GEC to water pipe and another to rod and also direct buried cable would come up underground into Panel P per NEC 2014 section 110.27 would fence be required where Panel P is?
3. What are the maximum height requirements from above floor in NEC 2014 for Panel P?
4. I have one outside feeder going to feed the cluster divided by firewall. Would this be in compliance with NEC 2014 section 225.30 or not?