Fred B
- Upstate, NY
- Electrician
What is the rationale for the not permitted use found in 334.12(A)(2) "Exposed within a dropped or suspended ceiling cavity.....l"
That was just part of the "horse trading" when the 3 story limitation was removed from the code. There was not enough votes for removing the 3 story rule, without adding some restriction.What is the rationale for the not permitted use found in 334.12(A)(2) "Exposed within a dropped or suspended ceiling cavity.....l"
So no rationale was used.![]()
Just like any other type of negotiation where you have two different view points.So no rationale was used.![]()
Can't see how this could ever be allowed on it's face. They should have atleast come up with a "legitimate" safety concern to substantiate a requirement, even if it could be debated.Just like any other type of negotiation where you have two different view points.
You had the non-metallic wiring method supporters on one side and the metal cable jacket and metal raceway supporters on the other side. There had been a push to get rid of the 3 story rule for a number of code cycles, and this restriction to get rid of the 3 story rule was the compromise that was worked out.
You could try a PI for the 2026 code to remove that restriction.
I agree. It seems this was one of those "it seems like a good idea" codes. Never really made sense to me why aluminum MC is considered to be so godly. The stuff isn't much tougher than NM in many ways. In fact I could see some situations where it is more of a fire risk than NM.Can't see how this could ever be allowed on it's face. They should have atleast come up with a "legitimate" safety concern to substantiate a requirement, even if it could be debated.
I am sure there were concerns brought up in the discussions. Not sure there were concerns that you can find in the published record. You can look at the published records for the 2002 code on the NFPA site. Not sure what exactly they will tell you.Can't see how this could ever be allowed on it's face. They should have atleast come up with a "legitimate" safety concern to substantiate a requirement, even if it could be debated.