- Wisconsin
- PE (Retired) - Power Systems
One thing that is rarely considered by people performing DIY AIC selection, is the requirement to make adjustments for when the short circuit X/R ratio differs from the one used in the UL listing for molded case breakers. Software packages like SKM show several short circuit values depending on the AIC 'range' of the molded case breaker, A high interrupting breaker, like a 22kA, may have been tested with a different X/R than a 10kA unit. The difference is not great so many people were taught to leave a fudge factor such as selecting a 65kA breaker even though the quick and dirty SCA result is 21kA.
Having to update or confirm arc flash calculations on a regular basis will often catch any issues resulting from utility changes (assuming someone revisits the available fault current).
I would guess that maybe 55-60% of the existing facilities, I have ever evaluated, have had at least some equipment that was inadequate for the realistic fault values I calculated.