Natfuelbilll
Please discuss use of 240.21(C)(4) for a transformer located indoors feeding a outdoor switch.
Can the AHJ approve the installation?
If the transformer is inside, part 4 of 240.21(C) does not apply. 240.21(C) applies to the conductors that are outside, originating from a transformer that is outside. When the transformer is inside, inevitably there will be a length of its secondary conductors that are also inside.
Vice-versa, the NEC makes an exception, allowing the OCPD/disconnect to be indoors immediately nearby the location where the secondary conductors enter the building. But it doesn't make an exception for indoor transformers feeding an outdoor switch, to allow you to have unlimited length of the conductors.
Not really. 90.4 permits the AHJ to waive specific requirements of the code, but only where " it is assured that equivalent objectives can be achieved by establishing and maintaining effective safety". Not sure that there is any way to do that given what the rule in 240.21(C)(4) permits and the fact that there are rules in 240.21(C) the do apply where the transformer is inside.Can a AHJ approve/sign off the indoor transformer installation?