12awg cable won't coordinate with 20A CB
designer82
Boston
For the life of me I can't understand why this #12awg cable overlaps the 20A breaker curve on the TCC and I can't get it to coordinate.
If I change it to a 30A cable, it will not overlap anymore or if I make the breaker 15A. None of that should be necessary with a #12awg cable and
20A CB though.
Any help is appreciated
You really have not provided much context, but when I look in the upper left of your graph it has a box that says Cable HV193 Ampacity with 3 red dots on the 15A line.
So my first question is: what about the installation conditions or software assumptions makes the system think the ampacity of a 12 ga cable is 15A?
Jon
All molded case breakers listed to UL 489 will always protect UL listed conductors, properly applied per the NEC, even though the TCC does not show it. This is partly why 4ft of conductor is included as part of the breaker testing procesure and set up.
You might check the cable details - it is set for copper right? THHN or something similar in conduit? Is there an ambient temp setting?
I agree with Jim, you shouldn't have to worry about #12 coordinating with a 20A breaker, but the plot of the wire does look like it goes farther left than it should.
The plots will never show small size conductors as being protected. It is a problem with the way conductor and breaker plots are created.
Follow the results from the actual testing.
Thanks guys much appreciated.
Yes the cable is set properly. #12 THHN, cu in conduit.
I understand what Jim is saying that it doesn't coordinate correctly on the software.
Bummer the customer will get the Etap auto-coordination print out that shows red on this branch. Oh well
Why even show the conductors on the TCC? Make sure your write up includes the explanation that conductor protection is demonstrated by the UL procedures.
EasyPower shows the entire #12 wire plot completely to the right of a 20A breaker curve from 0.2 seconds to 10 seconds. And the vertical long term wire rating is on the far right side of the breakers long time rating.
So I still think there is something wrong with the plot posted - the wire curve crosses into the breaker curve at 0.2 seconds, and stays there. And the long time plot is on the left side of the breaker curve.
Do you have the utility at 480V-3PH and similarly rated breaker?
I used a 208 volt utility and a QO breaker, but the voltage shouldn’t make any difference in this case.
If you have a system with multiple voltages, say 208V and 480 volts, if the 208v components are plotted on a 480 v scale, they will be shifted by a factor of about 2. But it doesn’t look like that’s what is happening in your case.