ElecTech83
- Senior Electronics Technician
Hello All! I work in an R&D Lab that uses several 480V pumps of varying sizes, being used to pressurize water. The one that is giving me headaches right now is a 7.5HP 480V 3 phase motor that is wired to an ABB ACS310 VFD. We are using it as a booster pump that is used to feed a much larger pump. We had the VFD wired to the motor just using standard SO cable (I know, this is a no-no) just to prove it would work, which it did. Then we had an electrician come in and mount the VFD enclosure to a wall and install permanent wiring. The electrician ran flexible steel conduit from the VFD to the motor and used solid core 12 AWG THHN wires for both the enclosure power and the VFD output to the motor. This seemed very strange to me, as in all my 12+ years of working with industrial controls I have never seen solid core wire used on a motor. The drive is randomly giving us "Overcurrent" faults and I am certain that the wiring is to blame - I believe we are seeing the charged capacitance of the extremely thin THHN insulation on the VFD/motor conductors discharging back to the VFD. I know that using an actual shielded VFD cable is the correct thing to do here, but I am wondering if I could just run (3) 12 AWG stranded RHH/RHW-2 wires from the VFD output to the motor through the existing steel conduit? I believe the wire I bought was intended to be used for PV (photo-voltaic) applications, but I think it should work. Thoughts?