New to mini split

Status
Not open for further replies.

StephenChryn

Member
Location
New Hampshire
Occupation
Electrician new construction
I’ve got this mini split system going into an apartment building that has 1 condenser, 4 heads, and a branch box. My question is I’m feeding main power to condenser and then come off condenser to power the branch box. I have to run #8 to condenser but if the condenser has fuses for the power out at 6amp I can run a smaller wire to the branch box correct? I was thinking #12 (I know that’s large for 6 amp but gc doesn’t want anything run smaller).
 
the #8 is likely oversized but without nameplate data that's a guess Here we usually see #16 or #14 to the interior units, often TC-ER depending on the wiring methods allowed.
 
the #8 is likely oversized but without nameplate data that's a guess Here we usually see #16 or #14 to the interior units, often TC-ER depending on the wiring methods allowed.
Thank you. I was hoping to do that. Unfortunately I’ll have to run #12 cause the gc doesn’t want anything smaller pulled. Even between heads we had to pull 12/3 waste.
The name plate data is
min circuit amp is 42
Max over current protection 50.
 
Big mini !!! Be careful, at MCA of 42 amps, #8 NM would be undersized.
 
RU sure the branch box is powered off the condenser? I have always seen them as taking an independent circuit.
Yes in the instructions there was 2 ways you could wire it. One like you said with a separate circuit but the the other way was coming off of condenser. Luckily it had the second option. I wasn’t there in the beginning the original foreman got fired and he pulled a lot of this already. Then they brought in the new foreman who then wanted me as his second and we’ve been fixing mistakes since we’ve been there.
 