short circuit calculation with motor contribution
hhsting
Glen bunie, md, us
Junior plan reviewer
Does anyone know of free good calculator or free software for short circuit fault current calculation and gives motor contribution also? I have POCO xfmr fault current secondary
I do not know that such a program exists, but if you post the info or PM me I'll run the calc for you.
Ok here goes:
Poco secondary xfmr 65ka fault current. 208/120V three phase. Need short circuit calculation following points:
1. Switchboard: located 14 feet away from POCO transformer secondary 65kA fault current. Service entrance cable 9 sets of 500kcmil AL direct buried.
2. Panelboard DP: located 75 feet from switchboard with direct buried 4 sets of 350MCM AL
3. Meterstack 1: located 142 feet from panel DP with feeder 2 sets of 500 MCM AL in conduit
4. Meter stack 2: located 149 feet from panel DP with feeder 2 sets of 500 MCM Al in conduit
What are the fault currents at above 4 points?
Ok here goes:
Poco secondary xfmr 50kA fault current. 208/120V three phase. Ineed short circuit following points:
1. Switchboard: located 14 feet away from POCO transformer secondary 50kA fault current. Service entrance cable 9 sets of 500kcmil AL direct buried.
What are the fault currents at above 4 point?
I don't have the software, but I know that if you want to include the motor calculation you will need to provide the motor specs....
*grin*
Jon
*grin*
Jon
For now regular fault current calculation. I need to compare what is regular with what is provided in plans
Have you looked at the calculator from Schneider Electric? It can handle motor loads.
Use PVC (non-metallic) conduit for direct burial applications.
Ok here goes:
Do you have motors?
  • Fault Currents.pdf
I would suggest that you proceed down this road very carefully from a liability standpoint.
These numbers should be developed by an engineer. As a plan review person, if you start "engineering" to confirm the numbers and the is an error you might be opening your self up to liability.
I am an engineer, licensed in the state that hhsting resides in. He gave me the parameters and I provided the calculation.
But, to your point, I don't expect hhsting to use my 5-minute fault current calculation to make design decisions. There are numerous parameters that go into the calculation and would need to be verified, like the Utility contribution with X/R ratio (likely not 65kA), the cable length and type, ...