Shahzad
- Canada and USA
- Electrical Engineer
Hi everyone,
I am working on a project for a client in Chile, where the 3 phase low voltage supply is 380V, 50 Hz, and Medium voltage is 13.2kV. The client is going to install an Electric heater for some industrial process which is almost 300 ft away from MCC room. The load of electric heater given by process engineering team is 500kW and now I have to figure out the power supply. I am wondering what size of voltage supply and breaker size should be used for such pure resistive load? From options point, I see below, but not sure at the moment which one will be cost effective and feasible.
(1) 500kW load, at 380V, 50Hz, the required Full load amps= 760.5Amps, so with 125% factor, I guess I would need 1000A in 2000A Frame, 380V, thermal mag insulated case circuit breaker (ICCB) from low voltage switchgear breaker, correct?
(2) Not sure if I will be able to find spare space in the 380V switchgear that could feed that big a single load. Is it possible and viable to have a breaker breaker in such size will not cause dip on the transformer upon start up?
(3) Would it make sense to feed the 500kW load from MV supply 13.2kV? Though, I will have to buy a step down transformer 13.2kV (Delta) / 380V (star), ad then feed the 500kW heater from the step down transformer?
Would appreciate if any one has come across similar problem in load sizing and has any suggestion?