Dark Sparky
- USA
- Electrical Engineer
A warehouse facility was designed (on paper) using an incorrect lighting fixture wattage, that was only ~40% of the actual fixtures' wattage. This was 3 years ago and to the designer's knowledge, no issues have been reported by the facility Owner. For context, this is LED high-bay, 277V dry warehouse lighting. Also aside, there are no lighting controls/switches - they use the breakers at the panel to switch these lights.
The worst-case circuit - designed to be a 20A breaker - is 6832 VA, so vs. an 80% load of 4432 VA, it's 154% of the breaker's capacity. (Even vs. 100% of a 20A breaker, 5540VA, it's ~23% over.)
Thoughts on why this design issue (built 3 years ago) may not have been reported as causing any issues? Of course it's possible that the electrical contractor installed 30A breakers, or split the circuits if they noticed the potential issue. Obviously as responsible designer/EE, one has a moral/safety obligation to notify the Owner. But this is a bit gray when no issues are (apparently?) occurring. So this is both a moral and engineering question. Any relevant insight or suggestions are welcome.