Grouch
 - New York, NY
Can the central inverter be on the rooftop?  or does it have to be located in the main service room?  anything in the NEC that dictates its location?
Central inverters are typically very large, like a few hundred KW minimum, but usually a meg or so. I have been out of commercial PV for a few years now, but 60 KW would be about the largest string inverter.Can a string inverter be considered a central inverter? When is the term 'central inverter' correct to use?
1. Where you said "Some string inverters offer the ability to use a combiner in the array field, and combine the strings in advance of connecting to the inverter."... wouldn't that be considered a central inverter? or would the low KW rating define it as a string inverter?
2. Where you said "Some central inverters have a built-in re-combiner to fuse or breaker the outputs as they are combined again"... The re-combiner would only be looking for the DC outputs of the combiners correct? in other words, you can't connect strings directly to the re-combiner; by definition a re-combiner only accepts the outputs of other combiners?
3. A central inverter without a built-in recombiner... it can only receive one input from a combiner? So one central inverter per combiner?
I guess a 4th question... are string and central inverters all available with MPPT's? Or it depends on the manufacturer?
Great stuff. Thanks for the replies.
My only follow-up question would be for #3: "Not necessarily. It could be that it is built for just one combiner, or it could be that it is built with the expectation that you'll use a separately-installed re-combiner adjacent to it on the pad."
So in either case, the central inverter only takes one input only? Whether through a combiner or re-combiner?
ah I see. I forgot about the inverters that have multiple MPPT's. so you can have many combiners, and their outputs connect to the MPPT's on one central inverter. Do i have that right?
back to the re-combiner... they can be adjacent or built-in? and say it's a built-in recombiner... that one output would typically go into one MPPT? So the recombiner connection to the MPPT would all be factory wired.