Wiring up a fire pump controller, which puts us in NFPA 70 Article 695 space, along with NFPA 20 (which article 695 references)
A fire pump controller can power auxiliary loads, such as a louver actuator, a beacon light, or local annunciator system. In these scenarios, we would tap off the incoming L/N and run wires through the controller's internal relays to achieve desired function.
For example, if we want the beacon light to turn on when the pump fails, we would run through the controller's pump fail contacts, etc.
NFPA 20 states (10.3.4.5.1)
A fire pump controller shall not be used as a junction box for any purpose (see section 9.7), including the following:
(1) to supply other equipment
(2) to splice incoming or outgoing wires
(3) to connect external surge suppression
9.7 is basically the same as NEC 695.6(I) junction boxes.
Based on these sections, would wiring these accessory loads (examples given - beacon light, louver actuator, local annunciator, etc) be a violation of NFPA 20? Obviously the this is subject to interpretation by the AHJ, but nobody likes getting into an argument if not needed.