Have a job coming up where I need to install approx. 100' of feeders for a ,400a panel, given the price of copper right now I'm probably going to use aluminum, the run will be done via existing aluminum conduit. Any issues with running aluminum feeders in aluminum conduit?


Sent from my SM-G986U using Tapatalk
 
Have a job coming up where I need to install approx. 100' of feeders for a ,400a panel, given the price of copper right now I'm probably going to use aluminum, the run will be done via existing aluminum conduit. Any issues with running aluminum feeders in aluminum conduit


No issue with aluminum feeders in aluminum conduit. The wire insulation separates it from the conduit.
 
The only possible issues I can think of are:
1. Conduit fill with the larger Al conductors. Compact stranded helps there, and
2. Need for Al rated terminations which is typically not a problem with panels.

Sent from my Pixel 4a using Tapatalk
 
As Busman said, if you are pulling standard conductors, 3" is too small. You are allowed (4) 700mcm in 3" if you use Compact Conductors.
 
As Busman said, if you are pulling standard conductors, 3" is too small. You are allowed (4) 700mcm in 3" if you use Compact Conductors.
I was using Table C8 and C8a - did I miss something? It looks like three conductors for either. Is this aluminum not rigid conduit?
 
I was using Table C8 and C8a - did I miss something? It looks like three conductors for either. Is this aluminum not rigid conduit?
I used C1 and C1a.... wasn't sure if he was using rigid or emt.
 