dwils1980
- Fort Collins Colorado
- Master Electrician, Building Inspector
210.8F requires all outdoor outlets to be GFCI protected. I’m running into issues with inspectors considering a spa panel with a 50amp GFCI breaker as an outdoor outlet and requiring the gfi be installed at the source to protect the hot tub and the spa panel. My argument is that the spa panel is listed as a main lug load center which I see as not requiring GFCI protection since any outdoor load centers would not require the GFCI protection. I’ve also used these same spa panels for AC condensers with a GFCI breaker feeding the condenser within the load center. I would like to know what other people’s thoughts are on this situation and if the article’s intent is to cover all outdoor electrical enclosures including load centers.