mbrooke
Batteries Included
- United States
- Technician
Say you're running some drivers at 208 volts. Do you run 3 single phase circuits or one 1 phase circuit? Which is cheaper?
I would want to know how many KW of lighting before giving an answer
I haven't seen a 3phase 208V driver.... but I have seen newer LED drivers with 208V 1-phase.One 3ph circuit.
Can I run them off 480/277 MWBC's? If I say Please?About 31.296 kw. 96 watt per troffer.
Well that is the common, but I have seen some drivers say specifically 208 1-phase.Correct, single phase. 120-277
You get slightly better copper use if you distribute your loads across 3 phases rather than have single phase circuits.
Say you have 6 wires carrying 20A. This is either 3 single phase circuits or 2 three phase circuits. This gives you: 3 x 208 x 20 = 12480 VA or 2 x 208 x 20 x 1.732 = 14,410 VA.
This difference is large enough to be significant, but is probably dominated by things like switching requirements.
Jon