AC\DC
Senior Member
- Location
- Florence,Oregon,Lane
- Occupation
- EC
Hello, I got a call this Monday to install some short runs of 3/4 pvc for some floor outlets and island in a 4" slab. I told them I would get to it today cause I was busy this week and next week. I forgot to mention they are pouring in 3 days and everything a rush, rush.
So The hole area is ready for Pour, I don't know why I was not called out sooner since this the plumber was done 3 month ago. Either last EC bailed or Homeowner was trying to do it themself and gave up. I just ran the pipe and secured it right on top of the rebar.
Home owner tell me that Concrete guy won't like that, ill have to go under the rebar and dig a small trench. I don't have a lot of experience with concrete encased conduits, will this cause problems in the concrete ?
I told the home owner " it will pass my inspection and no were in your 1 page plan you gave me does it state that conduits in slab must be under slab".
It would not take me long to just put it in under the slab. Though with this customer he comes at you from every angle and is rush, rush, mentality is making me mad. I am bidding the rest of the house. Though if I get it and don't put my foot down I feel he will be a constant bother the whole time.
I don't need the work so it's not a big deal if I make him mad.
1:Am I wrong in encasing the Conduit.? Will it effect the slab in those shallower areas
2:Should I just please the Home owner?
So The hole area is ready for Pour, I don't know why I was not called out sooner since this the plumber was done 3 month ago. Either last EC bailed or Homeowner was trying to do it themself and gave up. I just ran the pipe and secured it right on top of the rebar.
Home owner tell me that Concrete guy won't like that, ill have to go under the rebar and dig a small trench. I don't have a lot of experience with concrete encased conduits, will this cause problems in the concrete ?
I told the home owner " it will pass my inspection and no were in your 1 page plan you gave me does it state that conduits in slab must be under slab".
It would not take me long to just put it in under the slab. Though with this customer he comes at you from every angle and is rush, rush, mentality is making me mad. I am bidding the rest of the house. Though if I get it and don't put my foot down I feel he will be a constant bother the whole time.
I don't need the work so it's not a big deal if I make him mad.
1:Am I wrong in encasing the Conduit.? Will it effect the slab in those shallower areas
2:Should I just please the Home owner?