thanks, what power company. I have not done one like this in a long time.Our POCO has detailed drawings on grounding/bonding. Neutral is bonded to ct cabinet with large ground bar. Service GEC is landed in service disconnect.
Are you asking about the GEC?Who can tell me the proper places to ground between CT cabinet and out door panel. Both 600 amp. Will be using 2 ground rods 10' apart. Thanks
Thanks. Do you need bond bushings any particular place? All holes are punch cut, no concentric knockouts.Like infinity said, you need to be a little more clear about whether you are talking about where to connect the electrodes to or bonding between the two pieces of equipment.
Very briefly: the CT can is bonded to the service neutral conductor. However depending on the construction of the can and your POCO requirements, it might not be "directly" bonded to the neutral, and instead you may run a supply-side bonding jumper connected to the neutral at the service panels. See 250.64(D) for connecting grounding electrodes to services with multiple enclosures. I often like the gec busbar method, where you connect all the electrodes to a busbar and run a tap to each service enclosure.
thanksLocally, CT cabinet is bonded to the neutral as is the service panel. GECs are allowed from either but most often originate in the panel,.
If th cabinet has no provisions,a stud bolt kerney is often used.
yesAre you asking about the GEC?
thanksOur POCO has detailed drawings on grounding/bonding. Neutral is bonded to ct cabinet with large ground bar. Service GEC is landed in service disconnect.
Yes metal raceways enclosing service conductors need additional bonding besides a regular lock nut, see 250.92. Bonding lock nuts meet the requirement and IMO are easier than bonding bushings.Thanks. Do you need bond bushings any particular place? All holes are punch cut, no concentric knockouts.