Dsg319
- West Virginia
- Wv Master “lectrician”
What is your favorite way to calculate voltage drop of feeders/branch circuits.
I’ve always used 2 x k x I x D/KCMIL. Or a variant of to find max distance, size of conductor, or simply the voltage drop.
But as of recent I have just noticed that VD=IxR comes out to be just a tad bit higher of voltage drop. As an example using 2/0 copper , 200ampere load at 186’. VD=IxR came out 7.5vd compared to another calculation at 7.2Vd. I know it’s not enough to worry about.
And Obviously VD calculations are not based on the size of OCPD but rather the calculated load. I just used 200amp as an example for a single family dwelling voltage drop at worst case scenario.
Are there any reasons one calculation is more accurate than the other?
Also where do you start your distance for feeder/service conductors calculation. At the POCO transformer or “our service equipment”.
I’m going to make a guess and say our service equipment.