can you feed 2 vfd's from 1 disconnect? Here are the specs. 230v 3phase power. I have A 60amp breaker with #6g wire going into a 60A non-fusible disconnect.
Then was wanting to feed 2 vfd's with #10g wire out of the disconnect to 30a fuses for each vfd. The motors after the vfd's are rated for 26a fla. So 60a breaker(6g)>60a disconnect>(10g)30a fuses>vfd's(10g)>26fla motors. I hope I explained that right. Thanks for the help!