mbrooke
Batteries Included
- United States
- Technician
Does anyone know of a graph or calculations that would show the voltage sag of a transformer as current is increased on the secondary above the full load rating?
That sounds like a variation on a transformer impedance question.
I just did a "transformer impedance" search and found myriad results you can use, like "calculator."
This calculator shows a linear relationship with voltage drop to loading, but it does not go above 100%. I assume the voltage drop will continue to be linear above 100% until saturation started to occur
Transformer Calculator – Voltage Disturbance
voltage-disturbance.com
210609-2048 EDT
mbrooke:
I really do not understand your question.
To a large extent a transformer can be viewed for most loads as a linear circuit. Because of heating there will be changes vs time.
210609-2235 EDT
mbrooke:
The power rating of a transformer is a power dissipation factor relative to temperature rise, and thus failure point. It has virtually nothing to do with internal impedance other than how resistance changes, and at very high temperature the effect on magnetic characteristics of the core. But insulation failure will probably occur before major changes in core characteristics.
Take some electrical engineering courses.
Right. Saturation results from higher than designed magnetizing current, and this is independent of load current.Just a correction to something I said. I don't think saturation will occur from overloading. You would need higher voltage or lower frequency for that to happen.
Mbrooke,
A little though experiment to confirm voltage drop is linear:. Consider how transformer impedance is measured, and how that value is used to calculate secondary short-circuit current. We could not do this if it was not linear.