petersonra
- Northern illinois
- Semi-retired engineer
You need to understand that the disconnecting means to a control panel disconnects power for everything that the panel controls. And that's its intent. It's not intended to disconnect power to the control panel. That way you don't have to have disconnect switches on every freaking motor The control panel controls. Most of the time when you have a control panel like this if you have to shut off one motor you might as well just shut down the whole machine until you get it fixed. And it's also a good place to lock out the whole machine if you need to work on the machine. You don't have to go out and put 17 lock outs on to do some repair.I never understood the point of an integral disconnecting means.
There will always be power available on the line side of the control cabinet disconnect regardless of whether the disconnect is off unless you lock out the source.
Much like line side power to a shunt trip breaker on an MDP fed directly from a utility transformer.
Thousands of control cabinets are set up this way.
The disconnecting means in the control panel itself does not disconnect the power inside the enclosure.
JAP>