We have a submersible pump application (condensate knockout within a landfill gas header). Inside the vessel is classified Class I, Division 1.
The pump is supplied with flexible cord, factory terminated at the motor end. The flex cable will presumable run up and through the vessel cap, through a small Div 2 area, then to controls located in a non-classified area.
I believe what we have is similar to the application described in this post:
But I wanted to be sure I am understanding the conclusions correctly. Does this sound correct?
- Assuming the pump cable is factory sealed at the termination, then no seal needed at the pump end.
- Cable jacket is vapor-tight (another assumption), so there is no means for gas to enter the cable. As long as we carry the cable jacket through the cap and through the adjacent Div 2 area, then no boundary seal needed at either boundary.
- If we want a mechanical seal at the cable penetration, then a bulkhead connector or cable gland, similar to the devices referenced in the post above would be acceptable, even though they are not listed/labelled/specifically approved for Class I, Div 1 (or Div 2) applications.
As I write this I am realizing that this portion of the gas header may be at a negative pressure/vacuum - I'll have to think about whether the connector needs to prevent air passing into the header. But from an electrical code perspective, is it correct that a general purpose cable connector (I'm considering the sealcon) will work?
Thanks for any insights.