Romex and SER ampacities.
Someone I know called me about the size of wire needed for a new hot tub. It is a 6 person hot tub. I have not seen the tub or specs but the owner is looking for the info. The only thing he remembered was that somewhere it said it would draw 40A and need a 50A GFCI breaker. Does that make sense? If it draws 40A you could use #8 wire but would you use a 50A breaker? His question was probably in response to the huge increase in copper wire prices as I then looked and saw the price of 50' of 6/3 was $256 and the price of 8/3 was $169.
If it's NM cable you need #6 for a 50 amp OCPD.
Correct me if I am wrong...
The conductors from the OCP in the main panel to the disconnect are feeders, and as such, they may be sized for 100% of the continuous load + 125% of the non-continuous load. So, by my understanding of 215, 240, & 334, if the nameplate rating of the hot tub does not exceed 55A, then #6/3 NM may be used to the disconnect.
I agree with you . If 100% of non continuous load plus 125% of continuous load is 55 or less you can use #6 copper @ 60C ampacity on a 60 amp breaker.
Possible in that case 8-3 was older stock that hadn't had price increased yet? I'd expect them to be closer to one another than that. And if a 50 foot package at big box store they were pricey anyway even before copper went up. I could get a 50 foot cut piece at my electrical supply house for less than those prepackaged 50 foot pieces at a big box store. (this one doesn't cut anything smaller than 8 AWG so you buying at least 250 feet of 10 AWG NM cable or go to big box and pay higher price per foot if you don't want the leftover amount.
I know this has likely been beaten to death, but I'm happy to bring it up again. Correct me if I'm wrong; romex(nm) wiring is limited to the 60 degree column in table 310.16. So a 60 amp hot tub's disconnect could not be fed with 6/3 romex, but the load side to the tub could be #6 THWN. It's my understanding that the insulation on romex is rated higher than 60 degrees, but because it's part of a cable assembly it is limited. The same way that SER is comprised of individual XHHW conductors, but because it's part of a cable assembly it too is limited to 60 degrees.
Hoping we can put this to rest (yeah right). I see a lot of electricians with many more years in the field than me purchasing 8/3 for a 50 amp circuit and 6/3 for a 60. I'm pretty certain I'm correct on the romex issue, but I'm a bit unsure on the SER issue.
Thanks in advance all!
Article 338 does not have language like is found in 334.80 and is not limited to the 60°C ampacities.
Even where you use SE as interior feeder and branch circuit wiring, you are not limited to the 60°C ampacity. Where SE is used for interior feeder or branch circuits, the installation shall comply with the requirements of Part II of Article 334, excluding 334.80.
I have used 6/3 w/ground NM-B on hut tub installations before and protected it with a 2 pole 60 amp breaker. Unless I am missing something, Art. 240.4 (B) would allow this. #6 at 60 degrees C. has an ampacity of 55 amps, which is not a standard breaker size. Using the next standard size is permissible if (1), (2), and (3) are met.
That is true but sometime it is hard to find a 60 amp gfci. 50 amp gfci are much more available around here.
Now, have you ever read the instructions to the tub. Some state that the equipment grounding conductor must be full sized. You can't do that with nm cable that is why we always tried to pipe it.
I have not seen requirements for a full size ground on the few that I have done. That's not to say that both myself and the inspector have missed that. I have seen that all of the hot tubs' factory installed wiring bonds all metal non current-carrying parts with a #8 solid cu. conductor. Thanks for the input. I will check more closely on any future installations.
It has been awhile since I have seen them. Hopefully they got smart and changed their evil ways
For Massachusetts there is an amendment that only requires 60 degree column when installed in thermal insulation