Backcountry802
Member
- Location
- Vermont
- Occupation
- Electrician
I installed a generator hookup on a farm with a walk in freezer. The generator attaches to a tractor 3 point hitch and has 90A 240v rating.
When testing the generator we got it running, tested for voltage (244v) and transferred just the load for the freezer, the generator struggled for just a second or two when freezer inrush started, the the freezer operated on generator power for about twenty minutes. When power transferred back to utility power the freezer’s main contactor fried.
my understanding is that 240v motors do not have polarity, is the an inrush polarity that could have caused this? If I just swap the poles on the transfer switch from the generator does this have any affect on the freezer?
The freezer compressor is on a 50A breaker and only runs at 12.7a when active. This freezer had capacitor problems a couple months ago and the HVAC installer had to change them out.
When testing the generator we got it running, tested for voltage (244v) and transferred just the load for the freezer, the generator struggled for just a second or two when freezer inrush started, the the freezer operated on generator power for about twenty minutes. When power transferred back to utility power the freezer’s main contactor fried.
my understanding is that 240v motors do not have polarity, is the an inrush polarity that could have caused this? If I just swap the poles on the transfer switch from the generator does this have any affect on the freezer?
The freezer compressor is on a 50A breaker and only runs at 12.7a when active. This freezer had capacitor problems a couple months ago and the HVAC installer had to change them out.