gsanford
- Rockville, MD, USA
I read other posts on the forum but didn't really see a clear answer, so I wanted to start up another discussion on it.
New home construction. Room is designated as Laundry in plans, which in on the second floor room in a single family house. It's an enclosed room with a door. Electric washer and electric dryer. In the room dedicated 240V circuit for the dryer. There is a 120V outlet for for the washing machine and another 120V convenience outlet on the opposite wall mounted 18 inches off the floor. Both 120V outlets are on the same circuit, which I think is wrong and should be on separate 20A circuits.
My understanding of the code referenced below is the washing machine is on its own 20A circuit per 210.52(F) with the informational note in blue that is providing clarification on this section. The convenience outlet should also be on its own 20A circuits per 210.11(C)(2) since it clearly states additional 20A branch circuit.
So my main question is for the only two 120V outlets in the room, it should be on seperate 20A circuits or am I wrong with my interpretation?
This part of the code hasn't changed for at least the past decade that I know of, since I went and looked at all the code years back to 2011.
210.11(C)(2) Laundry Branch Circuits. In addition to the number of branch circuits required by other parts of this section, at least one additional 20-ampere branch circuit shall be provided to supply the laundry receptacle outlet(s) required by 210.52(F). This circuit shall have no other outlets.
Exception: When the 20-ampere circuit supplies a single bathroom, outlets for other equipment within the same bathroom shall be permitted to be supplied in accordance with 210.23(A)(1) and (A)(2).
210.52(F) Laundry Areas. In dwelling units, at least one receptacle outlet shall be installed in areas designated for the installation of laundry equipment.
Exception No. 1: A receptacle for laundry equipment shall not be required in a dwelling unit of a multifamily building where laundry facilities are provided on the premises for use by all building occupants.
Exception No. 2: A receptacle for laundry equipment shall not be required in other than one-family dwellings where laundry facilities are not to be installed or permitted.
A laundry receptacle outlet(s) is supplied by a 20-ampere branch circuit that can have no other outlets. See 210.11(C)(2) for further information.