Could it be for 3 phase and a reduced neutral?
The 2/0 EGC is colored green in the cable assembly.Could be for paralleling multiple sets to make a larger feeder.
One of the 4/0's has a white stripe to denote the neutral. I would think single phase installs would be the common use?Could it be for 3 phase and a reduced neutral?
That's another possiblity. I didn't do the calculation but the ratio of #4/0-#2/0 seems like a big increase in the EGC size.The only thing I can think of is section 250.122(B)
Even with 250.122(B) the egc would be 6awg copper or 4 awg aluminum. It's just confusing as to why the egc is so big in this case.That's another possiblity. I didn't do the calculation but the ratio of #4/0-#2/0 seems like a big increase in the EGC size.
I'm 99.999% sure that has nothing to do with it. If it was they would use larger EGC's for NM and MC cable.Cable manufacturers found out that with longer runs, breaker opening times increased, and with that EGC heating.
In short its to prevent the EGC from melting.
I have always been under the impression the EGC in SE cable is sized for use as a grounded conductor. I doubt 4 conductor cable gets used that way often so not sure why they don't offer 2 options.
Sometimes I install pipe and wire instead of 4/0 SER to avoid having to deal with the oversized BARE wire.
The NEC requires full size EGC for circuits 30 amp and less.They already do. #14 -#10 comes with a full size EGC.
But to answer larger sizes of NM and MC cable is rarely run more than a few hundred feet. Thus it is unlikely a manufacturer has ever had such an issue brought to their attention.
Could be single phase where full size neutral is required. (maybe 120/208 three wire)One of the 4/0's has a white stripe to denote the neutral. I would think single phase installs would be the common use?
There is no reason to bring anything to the manufactures attention. The NEC and UL have no issue with current EGC sizing. You are the only one that thinks its a big problem.
If I may, citing one of my sources, the IEEE Green Book:
Real world example of an overheated EGC:
I can show you the math if you like, but to keep things simple the more time an EGC carries current the hotter it will get. Long runs like those found in mobile home parks and rural pedestals increase breaker opening time due to the added impedance of the wire run itself.
Please do.
(1) Short-Circuit Formula for Copper Conductors
(I2/A2)t = 0.0297 log10 [(T2 + 234)/(T1 + 234)]
(2) Short-Circuit Formula for Aluminum Conductors
(I2/A2)t = 0.0125 log10 [(T2 + 228)/(T1 + 228)]
where:
I = short-circuit current in amperes
A = conductor area in circular mils
t = time of short circuit in seconds (for times less than or equal
to 10 seconds)
T1 = initial conductor temperature in degrees Celsius.
T2 = final conductor temperature in degrees Celsius.
Copper conductor with paper, rubber, varnished cloth insulation,
T2 = 200
Copper conductor with thermoplastic insulation, T2 = 150
Copper conductor with cross-linked polyethylene insulation, T2
= 250
Copper conductor with ethylene propylene rubber insulation, T2
= 250
Aluminum conductor with paper, rubber, varnished cloth
insulation, T2 = 200
Aluminum conductor with thermoplastic insulation, T2 = 150
Aluminum conductor with cross-linked polyethylene insulation,
T2 = 250
Aluminum conductor with ethylene propylene rubber insulation,
T2 = 250
Please do.