100% Rated Power Circuit Breakers?
xptpcrewx
Power System Engineer
Las Vegas, Nevada, USA
Licensed Electrical Engineer, Licensed Electrical Contractor, Certified Master Electrician
Does anybody know if Power Circuit Breakers and the associated Switchgear assembly are by default rated for 100% operation? Thanks in advance!
IIRC, ICCB and power CBs are 100% rated typically, while MCCB ar usually, but not always 80% rated.
But that might vary by manufacturer.
I agree.
The replacements for ANSI rated switchgear are 100%. But most manufacturers also offer a similar switchboard construction which is 80%.
Typically but not always? I assume this would be in the listing of the product?
To mix things up a bit, how would one go about determining if AKD-5 switchgear installed in the early 70's is 100% rated or not?
Check the ANSI specification it was built to.
If you know it was ANSI gear then it was 100% rated.
If it has a UL (81?) label then it was 80%.
Thanks. AKD-5 switchgear doesn't have a nameplate or label to indicate anything other than the Requisition and Summary No. This gear was manufactured from 1960 to 1977. How would I go about checking if it is ANSI gear or listed equipment?