mbrooke
Batteries Included
- United States
- Technician
Please do.
Now, 1,500 amps. 120 volts / 1,500 amps = 0.08 ohms loop impedance.
According to the values in chapter 9 table 9-
250 AL has an X of 0.041 and an R of 0.085 per 1000 feet
2/0 AL has an X of 0.043 and an R of 0.16 per 1000 feet
0.0378 ohms at 300 feet
0.0609 ohms at 300 feet
Adding to 0.0987 ohms or 1,215 amps
A simple 300 foot run easily places typical breakers into a 5-10 second clearing time which exceed the short time withstand of code minimum EGCs.
To put it bluntly a half size EGC simply can not overheat, where as 250.122 assumes the breaker will trip within its magnetic threshold as with most runs inside a building. Now If you've got the fault current there is nothing wrong with 250.122 and thats why code lets you go that small. Otherwise adiabatic limts come into play.