olly
- Berthoud, Colorado
- Master Electrician
I have an air conditioner, the name plate says max breaker size of 25A. I can get by with #12 CU since its a motor, is that right?
Its 17A. THHN / THWN-2 in LFNCWhat is the MCA (minimum circuit ampacity) on the name plate, and what is the wiring method?
Cheers, Wayne
#14 would be acceptable, so #12 is fine.Its 17A. THHN / THWN-2 in LFNC
Isn't most LFNC limited to 60C in wet areas, so that #12 would be required for the MCA of 17A?#14 would be acceptable, so #12 is fine.
I believe that you're correct.Isn't most LFNC limited to 60C in wet areas, so that #12 would be required for the MCA of 17A?
Cheers, Wayne
Cheers, Wayne
I would like to see that section if anyone knows it. I don't see it in the 2017I believe that you're correct.
It says it right on the side of the LFNC.I would like to see that section if anyone knows it. I don't see it in the 2017
356.12(2). There is similar language for all of the non-metallic raceways.I would like to see that section if anyone knows it. I don't see it in the 2017
Doesn't MCA mean minimum circuit ampacity? The ampacity of #14 AWG in 60C rated LFNC is only 15A.However you would base the conductor temperature on the actual operating load and not the MCA. With an MCA of 17, the actual operating load on a 14 AWG would be below its 60°C ampacity.
Yes it does mean minimum circuit ampacity, but that is ~25% greater than the actual running current. The heat in the conductor is created by the actual running current and not by the inflated current required by the NEC and the product standards.Doesn't MCA mean minimum circuit ampacity? The ampacity of #14 AWG in 60C rated LFNC is only 15A.
Cheers, Wayne
I have never noticed thatIt says it right on the side of the LFNC.
I get what you are saying but if the unit says minimum cir. amp is 17 then I don't get why a conductor at 15 amps is allowed.Yes it does mean minimum circuit ampacity, but that is ~25% greater than the actual running current. The heat in the conductor is created by the actual running current and not by the inflated current required by the NEC and the product standards.
The conductor doesn't have an ampacity of 15A. The section doesn't say the ampacity of the conductor must be based on the 60C column. It says the conditions of use can't exceed a 60C operating temperature.I get what you are saying but if the unit says minimum cir. amp is 17 then I don't get why a conductor at 15 amps is allowed.
Sorry, what distinction are you drawing here? Doesn't the 15A 60C ampacity of #14 Cu mean that for design purposes, #14 Cu carrying 15A continuously could reach 60C in temperature, assuming an ambient temperature of 30C and various other worst case conditions that go into the design numbers?The conductor doesn't have an ampacity of 15A. The section doesn't say the ampacity of the conductor must be based on the 60C column. It says the conditions of use can't exceed a 60C operating temperature.
Cheers, Wayne
As Don mentioned, It may not be carrying 15A continuously...it could be carrying less than 15A and therefore not reach 60C.Sorry, what distinction are you drawing here? Doesn't the 15A 60C ampacity of #14 Cu mean that for design purposes, #14 Cu carrying 15A continuously could reach 60C in temperature, assuming an ambient temperature of 30C and various other worst case conditions that go into the design numbers?
Cheers, Wayne
Sure, it may not be. But the A/C unit label calls for a conductor of a size that can carry 17A continuously. #14 Cu in LFNC can't do that without violating the 60C rating of the LFNC.As Don mentioned, It may not be carrying 15A continuously...it could be carrying less than 15A and therefore not reach 60C.
The mca of the conductor has nothing to do with the operating temperature of the conduit. The actual load current and the ambient conditions affect the operating temperature of the conduit.Sure, it may not be. But the A/C unit label calls for a conductor of a size that can carry 17A continuously. #14 Cu in LFNC can't do that without violating the 60C rating of the LFNC.
Cheers, Wayne