pvgreeze
- Philadelphia
- Electrical Engineer
Hi everyone,
I'm sure this question has been asked many times before, but I'm struggling to find resources & explanations for OCPD sizing and coordinating with transformers for PV arrays. I'm familiar with standard transformer OCPD sizing as per NEC Article 450, but I'm confused because NEC Article 450 requires sizing OCPDs for the transformer rated current. Now, this makes perfect sense if the transformer is feeding a load, but as a PV source, wouldn't it make the most sense to size the OCPDs for the rated output of the inverters?
I ask because numerous designs that I have started working on require unconventional transformer sizes (mostly between 45kVA - 75kVA). Instead of requiring custom transformer sizes, would I be able to specify a 75kVA transformer for (as an example) 50kVA of connected PV, and size the OCPD accordingly (ignoring inrush)?
I'm also quite confused by NEC 690.9(D) (for the 2017 NEC) and the requirement that both sides of the transformer be considered the 'primary' as opposed to the PV side and how that relates to OCPD sizing. Does this just exist to say that both sides of the transformer need OCPD protection, and that both sides have a 250% maximum rating?
I know this a lot, and probably a common topic of discussion here, but I would appreciate any help & feedback or explicit code guidance for coordinating PV output with transformer sizing and transformer OCPD sizing.
Thanks!
-pvgreeze
Thanks!
-pvgreeze