T T74 Member Location MA Jul 17, 2021 #1 Going under a road with PVC for a service. I have not seen anything that says Schedule 80 is required. Curious what other people use in this situation?
Going under a road with PVC for a service. I have not seen anything that says Schedule 80 is required. Curious what other people use in this situation?
Greentagger Senior Member Location Texas Occupation Master Electrician, Electrical Inspector Jul 17, 2021 #2 Schedule 40 is compliant per NEC. If you’re installing for POCO, verify their requirements.
T T74 Member Location MA Jul 17, 2021 #3 Greentagger said: Schedule 40 is compliant per NEC. If you’re installing for POCO, verify their requirements. Click to expand... Thanks, they only specified schedule 80 for the riser on the pole
Greentagger said: Schedule 40 is compliant per NEC. If you’re installing for POCO, verify their requirements. Click to expand... Thanks, they only specified schedule 80 for the riser on the pole
petersonra Senior Member Location Northern illinois Occupation Semi-retired engineer Jul 17, 2021 #4 It's going to be 4 ft down in the ground or maybe it's 3 ft and I don't remember off the top of my head. By the time it gets that far down it probably doesn't matter a whole lot what schedule it is it's pretty well protected by the ground.
It's going to be 4 ft down in the ground or maybe it's 3 ft and I don't remember off the top of my head. By the time it gets that far down it probably doesn't matter a whole lot what schedule it is it's pretty well protected by the ground.
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Jul 17, 2021 #5 How much more would Sched 80 be to use?