The proposed 2023 code has a rule requiring an overcurrent device in a separate enclosure for the service disconnect for services over 1600 amps. Does anyone else think this as written may require more than is needed for safety? For instance, 2 sections that have thick sheet metal in between them and with insulators around the bus to seal it would likely achieve the safety objective proposed here. But it seems the text requiring a separate "enclosure" may needlessly create difficulty. Wouldn't it be better if they said something like "the service disconnect shall be in its own section that is independently capable of sustaining all fault current likely to be imposed."
I might submit a comment but wanted to see if there was any insight here on this.
Secondly BTW: It would be nice if they would synchronize the threshold for some of these rules about large equipment. One size main for large equipment rules in 110.26, a different one for when to mark the clearing time in 110.16, one more for when to use arc energy reduction, one for when to use ground fault protection of equipment, and yet another now for when to use a separate enclosure. Many of these are rules where, having it at all levels may benefit but may be infeasible. So it's not like they can't settle on a common value for all these extra requirements.