Crossboss
Member
- Location
- Oklahoma city
- Occupation
- Journeyman wireman
For runs longer than 75 feet I need to upsize my wire? Can I pull #12 for the first 75' then upsize to #10. Is that an acceptable practice?
That’s not really correct, depends on your end load and percentage of voltage drop.For runs longer than 75 feet I need to upsize my wire?
I am guessing that is a spec. on the planThat’s not really correct, depends on your end load and percentage of voltage drop.
HUH? If I have 75' of #12 and 75' of #10, it matters not in what order they are connected; indeed, if we ignore splicing resistance, I can have 75 1' lengths of each with 149 splices and the voltage drop will be the same as with one 75' #10 and one 75' #12. The order is insignificant.That’s not really correct, depends on your end load and percentage of voltage drop.
When he said that’s not really correct. Maybe he was meaning the upsizing the conductors because of the given footage? As in possibly not needing to upsize the conductors depending on the load that will be at the end of the circuit.HUH? If I have 75' of #12 and 75' of #10, it matters not in what order they are connected; indeed, if we ignore splicing resistance, I can have 75 1' lengths of each with 149 splices and the voltage drop will be the same as with one 75' #10 and one 75' #12. The order is insignificant.
That statement is fundamentally incorrect. Code doesn't require upsizing for voltage drop. The answer to the implied question however, is much more complex. Do you understand ohms law completely? Please don't be offended by this question and don't feel you need to say yes here if you don't we are quite gentle to those who are looking to learn.For runs longer than 75 feet I need to upsize my wire? Can I pull #12 for the first 75' then upsize to #10. Is that an acceptable practice?
You really missed the mark here. Voltage drop relies on amperage, and resistance. Resistance depends on wire size, material and length. So Dennis, as usual is 100% correct wen he says, "depends on your end load and percentage of voltage drop." End load is the amperage you need for the above, percentage is obviously the accept or reject criteria. Your statement is not germane to his, even though it is correct.HUH? If I have 75' of #12 and 75' of #10, it matters not in what order they are connected; indeed, if we ignore splicing resistance, I can have 75 1' lengths of each with 149 splices and the voltage drop will be the same as with one 75' #10 and one 75' #12. The order is insignificant.
The response by AC/DC was to the OP stating that the run was over 75' then it needed to be increased in size.HUH? If I have 75' of #12 and 75' of #10, it matters not in what order they are connected; indeed, if we ignore splicing resistance, I can have 75 1' lengths of each with 149 splices and the voltage drop will be the same as with one 75' #10 and one 75' #12. The order is insignificant.
For runs longer than 75 feet I need to upsize my wire? Can I pull #12 for the first 75' then upsize to #10. Is that an acceptable practice?
Yes it is in the specs for runs longer than 75 to upsize.I am guessing that is a spec. on the plan
Yes it is on specs for runs longer than 75' use #10My point is 75 feet is not usually long enough to be an issue with voltage drop. I suspect this was a spec on the plans for that reason.
Pretty standard specification. On our current project they want it upsized after 85'.Yes it is on specs for runs longer than 75' use #10