PVC Junction Box
infinity
New Jersey
Journeyman Electrician (retired)
Are you permitted to use these boxes with a terminal adapter and a metal locknut?
The chances of a locknut becoming energized in a completely PVC surrounding would be slim to none in my book.
JAP>
Why do the locknuts need to be bonded? If I ran LTNM flex in and used an NM connector (with a metal locknut), I wouldn't have to bond it.
JAP>
I agree and I feel the same way about a pan head mounting screw inside of the but those aren't permitted either.
Maybe I'm overthinking this. I'm assuming that any metal part within the box would be required to be bonded.
Not trying to be a smart aft, but, do you bond the cover screws? They are actually on the outside where they can be touched.
I'm looking for feedback so nothing wrong with thinking outside of the box. The cover screws cannot contact the conductors inside of the box so there is no issue with them.
10-4. Don't know if this applies, or is legal, I have used a PVC reducer bushing into a PVC coupling with cement to secure pipe coming into a PVC box. 1x3/4 bushing into 1"coupling with 1x3/4 bushing to conduit. pretty watertight.
Not sure what you mean by this.
JAP>
JAP>
You cannot drill a hole in the back of the box and use screws to mount it.
314.43 Nonmetallic Boxes. Provisions for supports or other mounting means for nonmetallic boxes shall be outside of the
box, or the box shall be constructed so as to prevent contact between the conductors in the box and the supporting screws.
The reason the screws inside are not allowed is it affects the sealing of the box, water can enter at those points.
The code section I posted in post #12 states that the reason is "to prevent contact between the conductors in the box and the supporting screws".
So what section would require bonding of the locknut? One could, of course, use a grounding locknut if it is required to be bonded.
Cheers, Wayne