Mongothedog
- Midwest
- electrician
My state has adopted the 2020 code and is looking closely at services surrounding the 230.71B requirement in relation to meter stacks on a duplex or similar structure.
230.71B is pretty clear in the removal of the "6 disconnect rule" requiring each service disconnect to be in a separate enclosure, compartment, panelboard or have vertical separation. As soon as this monster change occurred two pack meters like a siemens unipak 2 gang 125 amp breaker combo were no longer allowed due to the two service disconnects being directly over one another. The 400 amp meter mains with a pair of 200 amp service disconnects under were also not allowed as the two service disconnects were in the same enclosure.
The fix should be that you put a main breaker before hand so that you have feeder disconnect now instead of a service disconnect. I figured this wouldn't be the end of the world but am now being told it has to be a factory main as part of the listed equipment as you can't just put a main in front of the service equipment. Is there a precedence for using non-factory mains before service equipment that can meet code then feeding a meter stack?