mbrooke
Batteries Included
- United States
- Technician
Couldn't we calculate this with Nehr-McGrath?
Sorry, I'm still inclined to disagree. The full definition of ampacity is "The maximum current, in amperes, that a conductor can carry continuously under the conditions of use without exceeding its temperature rating."
I don't find a definition of "condition of use" anywhere. If you can demonstrate that "conditions of use" means only "ambient temperature and number of current carrying conductors in a cable/conduit" then I will agree with you. Otherwise, I find it more rational to say that "conditions of use" includes temperature limitations of the conduit carrying the conductors. As well as possibly other limitations.
Which leads me to another ambiguity in the use of the word "ampacity": when the allowable current on a conductor is controlled by the temperature rating of one of its connections, terminologically, does that reduce the conductor's ampacity? Or is the ampacity still the same, and the termination limitation is an additional limitation? The distinction might matter for applying something like 240.4, "shall be protected
against overcurrent in accordance with their ampacities."
The wording of 240.4(D) "small conductors" is an example where the OCPD size is limited, but the language involved doesn't change the conductor ampacity. But 110.14(C) says "The temperature rating associated with the ampacity of a conductor shall be selected and coordinated . . ." Which suggests to me that the ampacity itself is changed by termination limitation.
Cheers, Wayne
Even if the LFNC is less than 3' or less?I believe that you're correct.
240.4D ocpd for wire size. In 310.15b16 the ** next to #14,#12
 point you to 240.4. These 3 wire sizes do not apply in motor wire sizing.I have an air conditioner, the name plate says max breaker size of 25A. I can get by with #12 CU since its a motor, is that right?
welcome to the forum and yes but for clarity I thing your last question should state these 3 asterisks do not apply to motor wire sizing.240.4D ocpd for wire size. In 310.15b16 the ** next to #14,#12
Not meaning that they do not apply, meaning that 240.4 states OCPD for 14,12&10, you cannot protect larger than 15a for #14, 20a for #12 and 30a for #10 copper respectfully. Thus with the AC in question, #10 copper should be ran and protected at 25a.welcome to the forum and yes but for clarity I thing your last question should state these 3 asterisks do not apply to motor wire
(D) Small Conductors.Not meaning that they do not apply, meaning that 240.4 states OCPD for 14,12&10, you cannot protect larger than 15a for #14, 20a for #12 and 30a for #10 copper respectfully. Thus with the AC in question, #10 copper should be ran and protected at 25a.
That's correct, the one caveat is using NM cable which limits the ampacity to 60° C. Run #12 MC and you can use a 25 amp OCPD.No that is not the case #12 can be run for the a/c as long as the wire is rated 75 C or 90C. Look at 240.4(G) which is referenced in 240.4(D)