hhsting
- Glen bunie, md, us
- Junior plan reviewer
Attached sketch has 1000A feeder from switchboard feeding meter stack that has 27 feeder breakers. Each feeder breakers feed one dwelling unit apartment panelboard.
Meter stacks is 22kA. The meter stack main breaker is 22kA and the meter stacks feeder breakers are 22kA. The meter stack is 3 tier series rating.
The unit panelboards are 22kA so all breakers in the unit panelboard are 22kA.
Each unit panelboard is MLO and has HVAC motor loads from one of the branch circuit breakers 30A.
In the sketch meter stack main breaker is labeled 1, one of the meter stack feeder breakers is labeled 2 and panelboard one of the branch circuit breakers is labeled 3.
I am trying to see if 3 tier series rating can be used or not between bkrs labeled 1,2 and 3 in sketch by using NEC 2017 section 240.86(C) however I do not know how to apply that since all those breakers are 22kA. Which one is higher rated overcurrent device and which one would be lower rated device?