Dealing with somewhat incomplete plans and unresponsive engineer, need to confirm a few things here quick- appreciate all help in advance:
Plans call for installing new service conductors to a distribution panelboard in an existing wellhouse -120/240V 3 phase.
1. New fused service disconnect at the pole will be 3-pole, 3-fuse with solid neutral & suitable for use as service equipment & install my MBJ here (Per 250.24 C)?
2. Cable schedule calls for "4 - 500KCMIL" from the pole disconnect to an existing panelboard in wellhouse. However with no other info provided, I'll just assume size the new fused main disconnect 400A rated & protect the ungrounded feeder (no longer a service) conductors with 400A fuses?
3. Underground run between service disconnect at pole and existing panelboard is now a feeder (as the fused disconnect at the pole is my service disconnect now) , so I need to add a #3 ground per table 250.122?