redikillowatt
- TX
I'm not sure this is the right forum (area) for this. I took electrical engineering in college, built & wired houses - using some fairly large tools.
Here, I'm talking 120V. I've used 15A tools on 12ga, 50 ft cords w/o problems. Most of the bigger motor tools I used weren't used continuously - that is a factor.
Now, have 2 corded electric - a 10A string trimmer & 12A edger. Both of these would be used for much longer stretches than a circular saw or sawzall. LOTS of people burn edgers / trimmers up.
Because of where several outdoor outlets are, I can reach a lot, but not all of the yard w/ one 50 ft cord. I have (2) 50 ft, 12 ga cords on hand.
Did a test w/ the smaller 10A string trimmer. With no load, there was 122+ V at end of 50 ft, 12 ga. That V likely will drop to 120V or bit less during the day, give or take.
Connecting a multi-meter & running 10A trimmer for a couple min., showed a steady 5 V drop (in 50 ft of 12 ga). So 4%.
I'm wondering how many volts below 120 is too much for the motors they use in these types of tools? A voltage that may not burn it up in a few uses, but is likely to shorten the tool's life?
That's 2x the V drop for 50 ft, 12 ga cords I've seen on several V drop calculators. I'll repeat the test using a 3 outlet mult-tap, for max contact of blades to female outlets - see if it makes a difference. I don't have much experience comparing actual V drops to theoretical calculators.
If the line voltage is 120 (not 122+), that's 115V. I'm not sure if that's wise. And I haven't tested adding 50 ft - or 25' more cord, nor tested the 12 A edger yet.
Mfg's manual shows cords for tools rated (roughly) 7.1 A - 12.0 A, for 50 ft - use a 14 ga cord. If there's (actual) 5V drop for a 10A tool on a 50 ft - 12 ga cord, it'll be more with a 14 ga.
I'll have to measure if 75 ft of cord would reach everything. Ext. cords ARE expensive!
If it would, not sure if 50 ft of 12 ga + 25 ft of 10 ga would work for 12A edger. Don't know I've ever seen a (good) 25 ft, 10 ga ext. cord. Might have to make it.
For the same amp range 7.1 A to 12.0 or 13 A, for 100 ft cord the manual says use 10 ga. Use 14 ga for 50 ft, but 10ga for 100 ft?
I'm not sure if 50 ft of 14ga is big enough for 12A edger w/ heavier load at times than a string trimmer.