electro7
- Northern CA, US
- Electrician, Solar and Electrical Contractor
I have 4 inverters: two at 120.3A and 90.2 max output current.
Total current: 421A x 1.25 (continous load) = 526.25.
Next size up breaker 600A.
Its a 3 phase 480V system and the interconnect is around 700ft away. I am running 3 sets of 3/0 thwn-2 conductors in individual conduits.
3/0 thwn-2 base ampacity is 225A at 90°C.
225A x 3= 675.
My question is if this installation is code compliant? 600A breaker with 3 sets of 3/0 thwn-2 copper conductors.
Since there is 4 current carrying conductors per conduit the ampacity of the wire goes down to 180A.
180A x 3 (sets of conductors)= 540A.
Is it okay to have that ampacity (540A) protected by the 600A OCPD?
I think this is okay since the total load is 421A (or would I use the 526.25A for continuous load to apply the ampacity of the wire?)
I think I am good on voltage drop being under 3%.
Next question is what size EGC do I run per conduit- do I use 250.122 for 600A OCPD wire size per conduit?
Thanks ahead of time.
Sent from my SM-N960U using Tapatalk
225A x 3= 675.