LouisianaApprentice
- Forest Hill, LA, USA
On a job i worked on i was reading the FLA off of units and calculating wire size. I told my jman all of them were under 30 when taken at 125% of FLA. Well he took that as only needing a 30 amp disconnect. The problem is the breakers used are oversized for the inrush so they are the MOCP rated on the unit. After digging through forums i saw where some people size a disconnect for calculated loads others say u have to use the size of which is greater (this being the breaker size which is 60). Will these 30 amp disconnects be acceptable for the condensers or do i need to size to the breaker.