Joe.B
Senior Member
- Location
- Myrtletown Ca
- Occupation
- Building Inspector
In general most electricians I've inspected for will add some 2X blocking within 12 in of where the feeder enters the subpanel, occasionally when it's not installed and I point it out it doesn't seem to be a problem, like they just forgot and they're happy to install it. I'm inspecting a new apartment building and each unit has a subpanel with a 4-wire feeder coming vertically through the stud bay and into the 100 amp subpanel (all electric units) through the top or bottom with more than 4 1/2 feet between top or bottom plate and the panel. I called it out as a correction and I used 334.30 Securing and Supporting. The electrician wasn't there when I did the rough inspection and when the GC gave him the correction the electrician just used framing nails bent over to "secure" the feeder to the inside of the stud bay. I said that I was pretty sure it needed to be an "approved" staple, cable tie, strap or similar and that usually I see it installed with blocking between the studs. He got huffy and decided that I was way off, and he may be right. I have no problem being corrected. I said I'd take some time to read the code and we would meet tomorrow. One thing he said is that 334.30 doesn't apply to feeders even though (in my mind) it's NM sheathed cable because it's a "feeder", ok I can understand that I could be wrong there but where should I be looking? It's not a service entrance cable, right? Any advice would be appreciated.