The double lug is fine as you are installing tap conductors to each panel which requires a main CB. The wire size #2 Al is only good for 90 amps as tap conductors so you'll need to use #1 Al.I use a double lug connecct to breaker in meter can which was the 200 Amp breaker then re used the seu 2 aluminum too 1 100amp breaker to main panel and add the same to the other 100 Amp panel and did use 4 ot aluminum for service
100 amp service and the tap rules are not the same. A 100 amp service can use the 83% rule which would allow #2 Al for the service. The tap rules require a 100 amp or larger conductor.That’s true but in RI they let you use 2 al for 100 amp service, I thought the tap rule would cover this it’s less ten 10 feet. The inspector pass the service and on the finish he said no, think him and the home owner had a few words and we were caught in the middle just trying to find code that would pass this again
If that rule is the same as the one in the NEC, you can't use it for two panels as it only applies to the conductors that carry all of the dwelling unit load.That’s true but in RI they let you use 2 al for 100 amp service, I thought the tap rule would cover this it’s less ten 10 feet. The inspector pass the service and on the finish he said no, think him and the home owner had a few words and we were caught in the middle just trying to find code that would pass this again
You don't have a (or two) 100 amp service(s); you have one 200 amp service.That’s true but in RI they let you use 2 al for 100 amp service, I thought the tap rule would cover this it’s less ten 10 feet. The inspector pass the service and on the finish he said no, think him and the home owner had a few words and we were caught in the middle just trying to find code that would pass this again
Read 230.72(A)I know I have a 200 amp service feeding 2 100 amp service. One 100 amp service is being fed from behind the meter can. The other 100 amp service is fed from meter can out from the side on the building and goes about 6 feet then goes into thr building to the 100 amp service.
That's what I thought of , too. That's why I agreed with Poweranytime post 14. That is such a common mistake especially in mid central west Indiana. I see it every where, Brand new inspections of buildings. Even the inspectors are not catching it. It's so crazy.Read 230.72(A)
Roger
No. You now have (1) 200A service with (2) 100A feeders/subpanels. Different items have different rules.I know I have a 200 amp service feeding 2 100 amp service. One 100 amp service is being fed from behind the meter can. The other 100 amp service is fed from meter can out from the side on the building and goes about 6 feet then goes into thr building to the 100 amp service.
Yes the terminology is critical in getting the correct answers.No. You now have (1) 200A service with (2) 100A feeders/subpanels. Different items have different rules.