Six of these fans

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
One 20A breaker, one branch circuit feeding direct wire six of these fans each fan is 120V, 1/20HP.



Do I need overload protection, motor controller at these fans, do I need to have each individual branch circuits to these fans or one branch circuit feeding six of them good?
 
This seems like test question
It’s all laid out in Art 430, you tell us what you think and we will check your answers
 
This seems like test question
It’s all laid out in Art 430, you tell us what you think and we will check your answers

I am guessing its in NEC 2017 section 430.53(A).

I am just not sure if the fan have overload protection and rating of fan controller in 450.53(A)(2)(3)??
 
Nor do we know as the site doesn't detail but I would say you are correct
 
Nor do we know as the site doesn't detail but I would say you are correct

But imagine if these fans are plugged in then and all circuits provided by 20A breaker.

However in my case its direct hard wire

Manufacturer instruction nor spec on that site say it either
 
Status
Not open for further replies.
Top