Fmkehoe
 - Cornwall ny USA
 - Inspector
Since my Ufer connection is going to be under earth, should I waterproof (tar, silicone, etc.) the acorn nut connection ?
			I've never seen rebar in a footing that is permitted to be in contact with dirt because it will corrode in a short period of time. The GEC should connect within the concrete.The rebar stub is connected to the rebar grid, encased in concrete. The #4 bare copper is acorn nutted to the rebar stub, and will, in a day or two, be back-filled over with dirt. Thus the connection is under ground.
I agree. Rebar is not listed for being buried in the dirt whether it is done that way or not in your area. It will corrode and you will lose that connection. Now if you can somehow protect the entire rebar then it may be fine..... Silicone the entire part that is stubbed out....I've never seen rebar in a footing that is permitted to be in contact with dirt because it will corrode in a short period of time. The GEC should connect within the concrete.
250.68(C)(3)
A rebar-type concrete-encased electrode installed in accordance with 250.52(A)(3) with an additional rebar section extended from its location within the concrete to an accessible location that is not subject to corrosion shall be permitted for connection of grounding electrode conductors and bonding jumpers. The rebar extension shall not be exposed to contact with the earth without corrosion protection.
Read it again. It says that the rebar extension must be accessible.Ahhh. So there it is. I just need to protect it from corrosion. Thank you all.
That is another good option. I will take it under advisement.Rebar should not be in contact with soil, it needs to be encased in concrete to protect it from corrosion. So I suggest getting a length of 8" Sonotube that is 3" taller than the rebar stub, centering it over the rebar, and filling it with concrete.
Cheers, Wayne
I like this solution given the scenario you describe.Rebar should not be in contact with soil, it needs to be encased in concrete to protect it from corrosion. So I suggest getting a length of 8" Sonotube that is 3" taller than the rebar stub, centering it over the rebar, and filling it with concrete.
Cheers, Wayne
Wait… if your an inspector you should know rebar isn’t allowed to stick out of the concrete…Well that’s what I want to do. I want to waterproof the entire 1 foot stub sticking out of the footing. I can slather tar on it and it will last forever. I just need to wait until the inspection is done so the inspector can see the connection. That’s what I’ll do I’ll just wait.
And IBC/IRC or whatever locally adopted version exists.Wait… if your an inspector you should know rebar isn’t allowed to stick out of the concrete…
rebar is required to have concrete cover by ACI 318
True, and those codes just say go by ACI 318And IBC/IRC or whatever locally adopted version exists.
I’m not an inspector. Not an electrical inspector anyway. That’s why I’m asking. I’ll just wait for the inspector to come and tell me. I won’t have that section back-filled.Wait… if your an inspector you should know rebar isn’t allowed to stick out of the concrete…
Why didnt the rebar come up beside a column?
I'd have to look in the IBC, but I suspect you're correct for that. IRC "R404.1.3.3.7.4 Support and cover." has it all spelled out without referencing ACITrue, and those codes just say go by ACI 318