I have fire pump 125HP 208V three phase. Trying to convert 125HP to kVA.
Based on NEC Table 430.250 125HP is 343A at 208V three phase.
343x.208x1.733=123.57kVA.
Now if I use calculator internet to convert assuming 100% efficiency and 0.8 PF then I get 116kVA.
Which is correct or both are incorrect? What should be used to convert when sizing panelboard load calculation?
Based on NEC Table 430.250 125HP is 343A at 208V three phase.
343x.208x1.733=123.57kVA.
Now if I use calculator internet to convert assuming 100% efficiency and 0.8 PF then I get 116kVA.
Which is correct or both are incorrect? What should be used to convert when sizing panelboard load calculation?