If I derate the MCB at a MSP w/ feed through lugs , should I still consider the potential of overloading the feed through conductors? On a regular panel, even if you derate the MCB, you would still need to install your PV breaker at the opposite end of the busbar from the MCB. But having feed through conductors kinda presents a whole different issue since you're technically not at the opposite end. Can I get some insight on this manner?