Ryan902
- Halifax, Ns
- Red Seal Electrician
Hello there, I recieved a call about lights that were not working in a theater that I service. I went over and noticed that there were two rows of LED lights, both fed from one breaker, but they were on seperate switches. The odd thing was, was that one strip was working fine and the other strip was burnt but (not completely, every one had a couple of flickering leds).
First thing I confirmed was that I was receiving proper voltage to all three phases and that I had no loose neutrals. Voltage to ground and the neutral bus bar were 120. (it's a 120/208v 3phase 4 wire panel).
Everything seemed fine. So I went to the first jbox and noticed they had shared neutrals for each 3 phase group (and some groups of 2 ungrounded) but all the neutrals in this jbox went to a common, giant splice of neutrals. I know normally you keep your neutrals seperate back to the neutral bus bar to avoid a shared neutrals between ungrounded ungrounded conductors on the same phase. But could this cause other problems? Especially when you're switching some lights off at the switch, creating an unintended path through the shared neutrals?
My guess is that either we had a surge of some sort, or there was some issue with these shared neutrals.
The panel was installed 7 years ago with no issues. My plan is to do the unfortunate task of seperating all mwbc neutrals back to the neutral bus bar.
Anyone ever encounter anything like this before? Thanks for your time.