EXISTING SERVICE
- Meter socket with underground service feed
- Main circuit breaker panel, 200A, located in basement, below meter socket. 2" PVC conduit between meter socket and circuit breaker panel. Existing panel is full with no spare breaker spaces.
WORK OPTIONS (I may be missing some and they may be out of proper sequence)
(1) meter main combo only with no branch circuit breaker spaces
- Remove and replace meter socket, land existing line and load conductors to meter socket lugs.
- Label exterior of new meter socket according to NEC2020 230.85 (3), "EMERGENCY DISCONNET, NOT SERVICE EQUIPMENT"
- Install 2 ground rods with #6 solid Cu conductor. Land conductor in new meter socket enclosure
--- OR ----
(2) mater main combo with 8 circuit breaker spaces, with feed-thru lugs for 200A
- Remove and replace meter socket, land existing line and load conductors to meter socket lugs.
- Replace conductors between meter socket and circuit breaker panel. Upsize because oUse 3/0 copper to allow reuse of 2" PVC conduit. Add in EGC, to make it a 4-wire feeder.
- Label exterior of new meter socket according to NEC2020 230.85 (1), "EMERGENCY DISCONNET, SERVICE DISCONNECT"
- Install 2 ground rods with #6 solid Cu conductor. Land conductor in new meter socket enclosure
- In existing circuit breaker panel, separate equip grounding and grounded (neutral) conductors. Remove bonding connection between enclosure and Neutral bar. Possibly, isolate the neutral bar from the metallic enclosure.
- "Extend" grounding electrode conductor (GEC) to new meter socket, service equipment. Likely, this is one conductor (#4 copper) which touches the incoming water supply pipe.
- install surge protective device (breaker type) in new exterior 8 space panel that is part of the meter.
I'm leaning towards OPTION 1 because of the lower cost and effort. I may or may not talk to the homeowner about these options. Of course, OPTION 2 gives some allowance for future expansion.