BradPV
Member
- Location
- North Carolina
- Occupation
- Residential PV Qualifier
If I tap a feeder to supply the PV system does the feeder then become a tap as well? The feeder is tapped in the combo panel but then the feeder is >10' from the load center.
I would say that segment C is directly addressed by (2017) 705.12(B)(2)(1)(b), and since that allowance doesn't place a distance limit, the limitations of 240.21 don't apply. Chapter 7 is implicitly modifying 240.21 there.One could definitely argue that the Wayne's section C of the feeder is a tap conductor as that term is used in 240.21(B) if the rating of the conductor (rounded up to the next standard OCPD) is less than the combined rating of the PV breaker and the subpanel in the main. It's just that that is reading between the lines, not something that's explicitly addressed in 705 of 240.
Although I agree, I'd probably settle out of court before taking that argument in front of a jury.I would say that segment C is directly addressed by (2017) 705.12(B)(2)(1)(b), and since that allowance doesn't place a distance limit, the limitations of 240.21 don't apply. Chapter 7 is implicitly modifying 240.21 there.
Cheers, Wayne
Nah, it's a slam dunk, as the next section specifically refers to 240.21(B). So it's clear that if the intention were to require segment C to comply with either 705.12(B)(2)(1)(a) or with 240.21, then 705.12(B)(2)(1) would say so, and subsection (b) wouldn't be there at all. Subsection (b) only makes sense as a replacement for the usual 240.21 requirements.Although I agree, I'd probably settle out of court before taking that argument in front of a jury.
I don't follow your logic at all. Under section (a) the conductor doesn't meet the definition of a tap conductor in 240 anyhow, so clearly 240.21(b) wouldn't apply. But if you choose to comply with section (b), 705 leaves the location of the OCPD vague. I've seen the question of where that OCPD is supposed to go get asked on the forum a number of times, and I've seen Mike Holt and his team briefly debate it in a video. Going back to 240.21(B) to answer that question is as valid as any other approach under the code, since as a general principle Chapters 1-4 remain in effect unless clearly modified by later chapters. There's no clear modification of that in 705. In fact, your comment about the next section seems backwards to me; that section is so badly worded and vague that it could be read just about any way one wants, e.g. to apply to our 'Section C' in question, if an AHJ were motivated to do so. Indeed, perhaps the general rejoinder is that nothing is a 'slam dunk' with certain AHJs when there's any room for interpretation in the code.Nah, it's a slam dunk, as the next section specifically refers to 240.21(B). So it's clear that if the intention were to require segment C to comply with either 705.12(B)(2)(1)(a) or with 240.21, then 705.12(B)(2)(1) would say so, and subsection (b) wouldn't be there at all. Subsection (b) only makes sense as a replacement for the usual 240.21 requirements.
Cheers, Wayne
A one line diagram would help clarify the situation, but I assume you have the following:
A main service panel, which qualifies on its own under (2017) 705.12(B)(2)(3) (that requirement must not be overlooked).. A breaker supplying a feeder to a subpanel. And a splice to that feeder of the output of a PV system. So the resulting spliced feeder just has 3 "ends". It has 3 segments, call them A from feeder breaker to splice, B from PV inverter to splice, and C from splice to subpanel.
Segment A can either carry grid current or PV current and needs to be rated for both cases. For interconnection without upsizing an existing feeder, the PV output (including 125% factor) has to be no greater than the feeder breaker, in which case segment A is protected in both case.
Segment B can also carry grid current (e.g. if it also supplies loads downstream from the grid, or if there's a fault), so segment B can be sized the same as segment A. Or if it can meet one of the tap rules in 240.21, that can be used; it still needs to be sized for the PV output.
Segment C can carry current from both the grid and the PV. For the grid only, it has to be at least the size of the feeder breaker (as it will be for an existing feeder). But since it now has multiple sources of supply, 705.12(B)(2)(1) gives you two options for protecting it: (a) size it for the sum of the supplies, or (b) have a main breaker in the subpanel to protect it from overload.
I think of 705.12(B)(2)(1)(b) as a sort of unlimited length tap rule for this limited situation, since the OCPD to prevent overload is downstream of the splice, which is the source of the second supply.
All of the above assumes an existing feeder that was full sized, i.e. not sized using the tap rules under 240.21. If interconnecting at a 240.21 tap, the situation gets more complicated; I've not thought out all the ramifications.
Cheers, Wayne

...
Disregarding fault conditions, ...
But aren't the tap rules all about fault conditions? I mean, if fault conditions didn't matter then OCPDs could be anywhere in any circuit, and tap length wouldn't matter a whit, but 240 doesn't allow that.
I think if the AHJ thinks that C (and for that matter, A) is a tap you really have to go outside what the code says and point out that the available fault current from the inverters is waaaay lower than the utility. Unfortunately the code kind of takes the opposite position with 705.12(B)(2), which says the inverter must be considered the same as the utility for 240.21(B) calcs. That section should probably be changed, but I don't know exactly how.
I guess my logic boils down to this: for the alternative possible intention of 705.12(B)(2)(1)(b) you posit, it could just read "(b) Compliance with 240.21(B) in accordance with 705.12(B)(2)(2)." The actual language is so far from that, reprising certain conditions and failing to reference 240.21(B), that it is providing a substitute for 240.21(B) for this situation.I don't follow your logic at all.
Sorry, how can Segment A possibly be considered a tap in any rational fashion? If its source of supply is the feeder breaker, it complies with 240.21(A). If its source of supply is the PV breaker, it still complies with 240.21(A). And both can't be true at once, contrary to what one misinformed AHJ may have once asserted to one of the members here.(and for that matter, A).
To rephrase that, segment C is what you say either needs to be compliant with a 240.21(B) tap rule based on 160A in this example, or be built with 160A of conductor. Is this correct?
Yes, I know, and I agree. But the code seems to be written as if these rare kinds of faults matter. I mean, suppose a 20ft tap is installed such that it complies with the 10ft rule but not the 25ft rule. How rare is the fault that doesn't trip the feeder breaker because of that? Probably more rare than the one you describe.If segment C is less than 10 ft or 25 ft, or if it is outside underground, all that would matter is that you are not depending on a next-size-up-rule or an 83% residential service conductor (feeder extension) rule, from what it would be by default. But if segment C is too long to be a tap, then it would need to be 160A. Given that 160A is not a standard size, this would mean that 240.4(B) could not govern its sizing. 240.4(B) could only apply if they add up to a standard size.
This seems like it is anticipating a very rare kind of fault, that is between 100A and 160A, such that it is in the blindspot of both the 60A fuse and 100A breaker combined. Given a grid-interactive inverter, it will only operate when the grid is present anyway, and the grid will feed a fault with a lot more than 160A.
Also, FWIW, 240.21(B) refers in the various subsections to "the rating of the overcurrent device protecting the feeder conductors." Absent 705.12(B)(2)(2), it wouldn't be clear how to apply that to segment C, in Carultch's example, should it be the 100A OCPD or the 60A OCPD?
Sorry, how can Segment A possibly be considered a tap in any rational fashion? If its source of supply is the feeder breaker, it complies with 240.21(A). If its source of supply is the PV breaker, it still complies with 240.21(A). And both can't be true at once,
I lost you here, it's 2017 705.12(B)(2)(2) or 2020 705.12(B)(2) that tells you how to interpret 240.21(B)'s "the rating of the overcurrent device" language when there are multiple sources of supply.705.12(B)(2)(3) says that the answer is 100A plus 125% of inverter output.
tl;dr Just skip to the last sentence of the body.Consider also that if there's a fault, A, B and C are all the same in terms of how much fault current could feed the fault. So if it makes sense to consider 'B' a tap, why not A and C?